CONFIG ADCX
Line 1,048: Line 1,048:
'setup the ADC-A converter
Config Adca = Single , Convmode = Unsigned , Resolution = 12bit , Dma = Off , Reference = Int1v , Event_mode = None , Prescaler = 32 , Ch0_gain = 1 , Ch0_inp = Single_ended , Mux0 = 0 'you can setup other channels as well
W = Getadc(adca , 0)
Revision as of 18:44, 7 February 2013
CONFIG ADCA | ADCB = mode, CONVMODE=sign, RESOLUTION=res, DMA=dma, REFERENCE=ref,EVENT_MODE=evt,  EVENT_CHANNEL=evtchan, PRESCALER=pre, BANDGAP=gap, TEMPREF=tref, SWEEP=sweep, CH0_GAIN=gain, CH0_INP= inp, MUX0=mux, CH1_GAIN=gain, CH1_INP= inp, MUX1=mux  , CH2_GAIN=gain, CH2_INP= inp, MUX2=mux, CH3_GAIN=gain, CH3_INP= inp, MUX3=mux
mode
sign
The conversion mode. This can be SIGNED or UNSIGNED. When choosing SIGNED you should assign the result to an integer. When choosing UNSIGNED you should assign the result to a word. The default is UNSIGNED.
When the ADC uses differential input, SIGNED mode must be used, when using single ended input both signed or UNSIGNED mode can be used.
Note:
• Conversion mode is configured for the whole ADC, not individually for each channel, which means that the ADC must be put in the signed mode even if only one of the channels uses differential inputs.
• Negative values are not negative inputs on the IO pins, but higher voltage level on the negative input in respect to the positive input. Even though the resulting value can be negative. For example +1.4 V on negative Input and +0.3 V on positive input is OK.
• Do not apply Voltages below GND or above VCC !!
res
The resolution of the conversion. Valid values are :
- 8BIT
- 12BIT. This is the default
- LEFT12BIT. This will result in a left aligned 21 bit value.
dma
If you want to use the DMA channel, you can select which DMA channels must be used:
- OFF (no DMA)
- CH01 (channel 0 + 1)
- CH012 (channel 0 + 1 + 2)
- CH0123 (channel 0 + 1 + 2 + 3)
ref
Selects the reference to use. Valid options :
- INT1V. For internal 1V reference
- INTVCC. For internal voltage divided by 1.6
- AREFA. External reference from AREF pin on PORT A.
- AREFB. External reference from AREF pin on PORT B.
gap
Enables the bangap reference. Use ENABLED or DISABLED.
Setting this bit enables the bandgap to prepare for ADC measurement. Note that if any other
functions are using the bandgap already, this bit does not need to be set. This could be when the
internal 1V reference is used in ADC or DAC, or if the Brown-out Detector is enabled.
tref
Enables the temperature reference. Use ENABLED or DISABLED.
Setting this bit enables the temperature reference to prepare for ADC measurement
sweep
Selects which channels are included in a sweep when a channel sweep is triggered by the event system or in the free running mode.
Valid options :
- CH0 : channel 0 included
- CH01 : channel 0 and 1 included
- CH012 : channel 0-2 included
- CH0123 : all channels are included
evtchan
Event channel selection. This selects which channel should trigger which ADC channel.
Valid options:
- CH0123. Event channel 0, 1, 2, 3 as selected inputs
- CH1234. Event channel 1, 2, 3, 4  as selected inputs
- CH2345. Event channel 2,3, 4, 5 as selected inputs
- CH3456. Event channel 3, 4, 5, 6 as selected inputs
- CH4567. Event channel 4, 5, 6, 7 as selected inputs
- CH456. Event channel 4, 5, 6 as selected inputs
- CH67. Event channel 6 and 7 as selected inputs
- CH7. Event channel 7 as selected input
evt
Event channel mode selection. This selects how many of the selected event channel are in use. Valid options:
- NONE. Event system is not used
- CH0. Event channel with the lowest number, defined by evtchan
triggers conversion on channel 0
- CH01. Event channel with the two lowest numbers, defined by
evtchan trigger conversion on channel 0 and 1 respectively
- CH012. Event channel with the three lowest numbers, defined by
evtchan trigger conversion on channel 0, 1 and 2 respectively
- CH0123. Event channel defined by evtchan trigger conversion on
channel 0, 1, 2 and 3 respectively
- SWEEP. One sweep of all active ADC channels defined by SWEEP on
incoming event channel with the lowest number, defined by evtchan
- SYNCSWEEP. One sweep of all active ADC channels defined by SWEEP on
evtchan. In addition, the conversion will be synchronized on
event to ensure a very accurate timing for the conversion.
pre
Prescaler value. The prescaler divides the system clock and applies it to the A/D converter.
Valid prescaler values :
- 4, 8, 16, 32, 64, 128, 256 and 512
gain
Each of the 4 channels can have a different gain. Valid values are :
1,2,4,8,16,32 and 64
inp
Each of the 4 channels can have a different mode. The 4 modes are :
- INTERNAL. For example for temperature measurement
- SINGLE_ENDED. For measuring positive voltages
- DIFF. For differential input without gain which allows to measure negative voltages.
- DIFFWGAIN. Same as DIFF but with gain.
mux
Selects the MUX to use with the channel. This must be a numeric constant.
The value depends on the mode. See details below under How to selcect the MUX to use with the channel.
At run time you can change the ADCx_CHy_MUXCTRL register. Where x is A or B, and y is the channel 0-3.
AVR XMEGA A
AVR XMEGA B
AVR XMEGA D
ADCA
Yes
Yes
Yes
ADCB
Yes
Yes
Channel 0
Yes
Yes
Yes
Channel 1
Yes
Channel 2
Yes
Channel 3
Yes
Architecture
Pipelined
Cyclic
Cyclic
Max ADC frequency
2MHz
1.4Mhz
1.4MHz
Single propagation ADC
cycles number (12 bits)
7
7
7
cycles number (8 bits)
5
5
5
Max sample per second
(12 bits)
2Msps
200Ksps
200Ksps
ADC result to DMA
Yes
Yes
SWEEP mode
(channel sweep)
Yes
Number of Internal inputs
4
3
3
Internal inputs
Temp, Vcc/10, Bandgap, DAC
x 0.5 Gain
Yes
Voltage reference = INTVCC/2
Yes
12-Bit =  [MSB , Bit 10 , Bit 9 , Bit 8, Bit 7 , Bit 6, Bit 5, Bit 4, Bit 3, Bit 2, Bit 1, LSB]
ADC Clock Cycle 1: Start Ch0 without gain
ADC Clock Cycle 2:  Channel 0 MSB (Bit11)
ADC Clock Cycle 3:  Channel 0 Bit9, Channel 1 MSB
ADC Clock Cycle 4:  Channel 0 Bit7, Channel 1 Bit9, Channel 2 MSB
ADC Clock Cycle 5:  Channel 0 Bit5, Channel 1 Bit7, Channel 2 Bit9, Channel 3 MSB
ADC Clock Cycle 6:  Channel 0 Bit3, Channel 2 Bit5, Channel 2 Bit7, Channel 3 Bit9
ADC Clock Cycle 7:  Channel 0 Bit1, Channel 2 Bit3, Channel 2 Bit5, Channel 3 Bit7
ADC Clock Cycle 8:  Channel 0 LSB
ADC Clock Cycle 9: Channel 0 conversion complete ......
ADC clock.
After four ADC clock cycles all 4 ADC channels have done the first sample bit (the MSB).
• Differential measurement without gain
  Pin 0...Pin 3 can be sleected as negative input
'      Pina.0 -----+ differnential|
'                  | without gain |
'      Pina.1 -----+     ADC      |
• Differential measurement with gain
  Pin 4...Pin 7 can be sleected as negative input
'                  | with    gain |
'      Pina.4 -----+     ADC      |
'       Vinp  -----+ single ended |
'                  | signed mode  |
'         GND -----+     ADC      |
• Single ended input (unsigned mode)
  In unsigned mode the negative input is connected to half of the voltage reference (Vref) voltage minus a fixed device specific negative offset
  This value also depend on the selected voltage reference so you should measure the real value by first selecting the voltage reference.
  (ΔV = Vref * 0.05)
  How to measure the offset ?
  Connect the ADC input pin (Vinp) to GND and measure the offset.
  This is also called offset calibration. This value can be stored for example in EEPROM and is therefore available for all other measurements.
  See also example below.
  This offset calibration value is then subtracted to each ADC output
  The offset enables the ADC to measure for example zero crossing in unsigned mode.
'                  | unsigned mode|
' (Vref/2)-dV -----+     ADC      |
• Internal input
Mux0 = &B0_0000_000
Bit 0...2 of MUX0 = MUX selection on negative ADC input (For internal or single-ended measurements, these bits are not in use.)
Input mode = INTERNAL:
MUX POSITIVE INPUT
Group Configuration
Description
0000
TEMP
Temperature Reference
0001
Bandgap
Bandgap voltage
0010
SCALEDVCC
1/10 scaled Vcc
0011
DAC
DAC output
For example:
W = Getadc(adcb , 0 , &B0_0011_000)                       'Measure DAC
Another example:
Ch0_gain = 1 , Ch0_inp = INTERNAL , Mux0 = &B0_0011_000 'configure MUX0 to measure internal DAC
Input mode = SINGLE_ENDED, DIFF or DIFFWGAIN:
MUX POSITIVE INPUT
Group Configuration
Description
0000
Pin0
ADC0
0001
Pin1
0010
Pin2
0011
Pin3
0100
Pin4
0101
Pin5
0110
Pin6
0111
Pin7
1000
Pin8
1001
Pin9
1010
Pin10
1011
Pin11
1100
Pin12
1101
Pin13
1110
Pin14
1111
Pin15
ADC15
Input mode = DIFF:
MUX NEGATIVE INPUT
Group Configuration
Description
000
Pin0
ADC0
001
Pin1
010
Pin2
011
Pin3
ADC3
100
reserved
reserved
101
GND
110
reserved
reserved
111
INTGND
inernal GND
Input mode = DIFFWGAIN:
MUX NEGATIVE INPUT
Group Configuration
Description
000
Pin4
ADC0
001
Pin5
010
Pin6
011
Pin7
ADC3
100
INTGND
internal GND
101
reserved
reserved
110
reserved
reserved
111
GND
GND
Example:
Ch1_gain = 1 , Ch1_inp = Diffwgain , Mux1 = &B0_0001_001
Positive Input =        PIN1
Negative Input =        PIN5
Calculation of ADC Value
G = Gain
TOP with 12-bit resolution:
• TOP value of a signed result is 2047 and the results will be in the range -2048 to +2047 (0xF800 - 0x07FF). This is 11-bit plus sign bit (+ or -).
• TOP value of of an unsigned result is 4095 and the results will be in the range 0 to +4095 (0x0 - 0x0FFF). This is 12-bit.
Vinp and Vinn =  the positive and negative inputs to the ADC
TOP = 2047
Vinp = +0.3V
Vinn = +1.4V
G = 1
ADC Resolution = - 1092
TOP = 4095
Vinp = +1.0V
G = 1
ADC Resolution = 2175
ADC Compare function
For ADC A you need to set register ADCA_CMP and configure the interrupt.
To configure the interrupt for example for ADC A Channel 0 the register ADCA_CH0_INTCTRL need to be set to:
• Compare Result Below Threshold
• Compare Result Above Threshold
ADC Calibration
Register ADCA_CALL = Low Byte of calibration value
Register ADCA_CALH = High Byte of calibration value
This ADC calibration value copy should be done in a setup routine before using the ADC.
See also READSIG (reads a byte from the signature area in the XMEGA)
ADC Clock Frequency
Don't confuse ADC Clock frequency with ADC conversion speed. So even if you set the ADC Clock frequency to 2MHz you can sample at a rate of for example 20KHz !
http://avrhelp.mcselec.com/notice.jpgTake care on the source impedance of the analog signal source. If the source impedance is too high, the internal sampling
capacitor will not be charged to the correct level and the result will not be accurate.
Additional Best Practise
• Switch off unused peripheral parts with CONFIG POWER_REDUCTION to eliminate noise.
• Put the XMEGA in the “Idle” sleep mode directly after starting the ADC conversion to reduce noise from the CPU
• Use the lowest gain possible to avoid amplifying external noise
• Apply offset and gain calibration to the measurement
http://avrhelp.mcselec.com/notice.jpgThe external reference pin AREFA or AREFB is shared with the DAC module !
For Maximum Performance use Event System and DMA Controller combined with ADC
See config DMA, config DMAchx, config Event_System
GETADC , CONFIG ADC, ATXMEGA
Example for Single Conversion
Example for Free Running Mode
'Configure ADC of Port A in FREE running mode
Config Adca = Free , Convmode = Signed , Resolution = 12bit , Dma = Off , _
Reference = Intvcc , Event_mode = None , Prescaler = 256 , Sweep = Ch01 , _
Ch0_gain = 1 , Ch0_inp = Diffwgain , Mux0 = &B00000000 , _
Ch1_gain = 1 , Ch1_inp = Diffwgain , Mux1 = &B00001001
' With MuxX you can set the 4 MUX-Register
' ADCA_CH0_MUXCTRL (for Channel 0)
' ADCA_CH1_MUXCTRL (for Channel 1)
' ADCA_CH2_MUXCTRL (for Channel 2)
' ADCA_CH3_MUXCTRL (for Channel 3)
' Mux0 = &B00000000 means in Signed Mode:
' MUXPOS Bits = 000 --> Pin 0 is positive Input for Channel 0
' MUXNEG Bits = 00 --> Pin 4 is negative Input for Channel 0 (Pin 4 because of Differential with gain)
' Mux1 = &B00001001 means in Signed Mode:
' MUXPOS Bits = 001 --> Pin 1 is positive Input for Channel 1
' MUXNEG Bits = 01 --> Pin 5 is negative Input for Channel 1 (Pin 5 because of Differential with gain)
With this example we want to measure the offset in single ended unsigned mode and also the output of the internal 1.0 Voltage reference to DAC B PINB.2. Also the signature row with calibration byte is in the example.
1. With the used ATXMEGA256A3BU the voltage on DAC B was measured with an DMM and the value was: 1.014V
2. After changing the gain calibration register of DAC B Ch0 to DACB_GAINCAL = 160 then the DAC B Ch0 analog output value was the expected 1.000V
3. The offset in single ended unsigned mode is 208
4. Now we connect the DAC B output (Pinb.2) to ADC B input (Pinb.0): the ADC resolution is 2180
5. Vref = 3.323Volt/1.6 = 2.076875 (Vcc was also double checked by a DMM)
6. 2.076875/4095 = 507.1733822 µV
7. 2180* 507.1733822 µV = 1.1056379 V
8. So here we see the difference of the DAC output 1.000V to the measured value in single ended unsigned mode of1.1056379 V is 0.10564 V
9. When we subtract now the offset from the measured result (2180 - 208 = 1972) we are getting closer to the DAC B output
10. 1972 * 507.1733822 µV = 1.0001V
Internal measure the DACB output with ADC B